Well-known Member
So the difference is they’d add an extra feed at the meter not split the existing feed from meter to CU? That I can understand if not like lol.
This is what our
latest installer did:
View attachment 1679710
Split the meter tails so existing red and black continued to the CU and the new brown and blue went to the charger. Interesting how much thicker the EV charger cables are than the ones that feed the whole house.
Thanks. This is exactly what I'm imagining but with the tail to the meter being rather longer.
That’s a great illustration and hopefully helps show what the majority of installers do. This avoids anyone needing to touch the existing CU at all, so no need to modify and test that part of the installation. Only the new works for the charger install then need to be tested/certified, and compliant with the latest electrical regs.This is what our
latest installer did:
View attachment 1679710
Split the meter tails so existing red and black continued to the CU and the new brown and blue went to the charger. Interesting how much thicker the EV charger cables are than the ones that feed the whole house.
That’s a great illustration and hopefully helps show what the majority of installers do. This avoids anyone needing to touch the existing CU at all, so no need to modify and test that part of the installation. Only the new works for the charger install then need to be tested/certified, and compliant with the latest electrical regs.
I think someone else picked up on it already but if the existing cable from the meter to the CU can't be inspected then that maybe why they want to run a new one?
If Motability are paying for the installation of a smart charger it might be worth getting the quote for the extra work and see if you think it's a worthwhile investment to pay the extra to get the charger for "free". I think the final bill for ours was £675 which was picked up by MG who were offering a free charger installation. .
I don’t really understand how the existing installation is set up, but I also don’t understand why people don’t take the opportunity of testing their existing installation, and then adding the ev charger to that?
If the meter point (this one looks like it needs some attention) is nearer, then just use them Henley Blocks as suggested.
If your renting from a farmer, they are notorious for having short arms and deep pockets.
Ok. You have to seek your energy suppliers permission, as there will be alterations to the meter tails, whose connections at the meter will be sealed.
What is the plan to supply the ev charger with this new distribution circuit?
Unless there's an upstream isolation switch, the supply fuse will need to be pulled and the meter tails cut. Hence the requirement to get supplier permission.How come? It would be connected between the meter and CU, like any other? The connection is at the CU end.
No idea that's for the installer to figure out if anyone bothers to turn up. I'm not a spark and not trying to be. Just want to understand where the problem is and why.
Unless there's an upstream isolation switch, the supply fuse will need to be pulled and the meter tails cut. Hence the requirement to get supplier permission.
You‘ll need the ‘seal fairy’ to cut the main seal. Some DNO‘s don’t even like electricians pulling their main fuses. Some DNO’s will install an isolator, for a fee. Which makes life easier.
I would ensure you employ a competent electrician, who can design, install and test this work for you. (and knows about ev installs).
I can try and give you some advice to know what you should be getting, pre warned pre armed. However, the best way forward is to get yourself a competent ev charger installer, but some more photos of your service head an cu might help. There’s other sparks on this forum that could assist…all Greek ?There may be a switch. Ok there is a switch but not looked where it is on the circuit. It will be a specialist but trying to get them here is the challenge.