AVForums

Our philosophy in our forums, reviews, podcasts and feature videos is to promote audio and visual excellence by gathering and sharing the best information and resources available.

Help

To begin please visit our help section »

Not a Member Yet?

It only takes a minute to start enjoying the benefits of AVForums membership, and it's free!

Member Log in

Chasing Walls

Post Reply
Old 10-03-2005, 12:28 PM   #1
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Chasing Walls

Hi Guy,

I plan to chisel a 40mm by 40mm channel in a load barring wall, The Channel will be 125mm long & running diagonally from just off centre to the bottom left of the wall,
This is to fit a 32mm Diameter tubing to enable me to change cable if I wish to in the future.

Can someone tell me if this channel will effect the stablility of the walls?

Thanks in Advance

Dan
  Quote
Old 10-03-2005, 11:08 PM   #2
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Anyone??

I hope to start this at the weekend
  Quote
Old 11-03-2005, 1:19 AM   #3
Member
 
surrey lad's Avatar
Join Date: Dec 2002
Location: Epsom Downs
Experience Points:
4,359, Level: 15
Points: 4,359, Level: 15 Points: 4,359, Level: 15 Points: 4,359, Level: 15
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 12, Got 18
Posts: 626
Go for it!

At 125mm long it doesn't really matter. I've just had a new extension/HT room built and the dividing wall which is by the way is Very stressed has had a 175mm ish x 125mm lutron back box along with many more cable chases cut into it with the permission of the local distric surveyer.


At the size you mention, have no fear!!!!
  Quote
Old 11-03-2005, 1:31 AM   #4
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Thanks for you advice, will go for it!!

Dan
  Quote
Old 11-03-2005, 9:53 AM   #5
Senior Moderator
 
Flimber's Avatar
Join Date: Sep 2002
Location: Yorkshire
Experience Points:
20,324, Level: 34
Points: 20,324, Level: 34 Points: 20,324, Level: 34 Points: 20,324, Level: 34
Activity: 43.6%
Activity: 43.6% Activity: 43.6% Activity: 43.6%
Thanks: Gave 2,913, Got 2,439
Posts: 9,358
You might want to drill a series of holes to more easily enable the knocking out any masonry and give you a cleaner line (your chisel just 'joins up the dots', in effect). An SDS drill would do that in seconds.

Mike.
  Quote
Old 11-03-2005, 9:55 AM   #6
Member
Join Date: Apr 2003
Location: Norwich, UK.
Experience Points:
5,512, Level: 17
Points: 5,512, Level: 17 Points: 5,512, Level: 17 Points: 5,512, Level: 17
Activity: 1.4%
Activity: 1.4% Activity: 1.4% Activity: 1.4%
Thanks: Gave 0, Got 3
Posts: 446
Just a point, although there's nothing to stop you, you shouldn't really channel cables in diagonally. This makes it very very hard for future residents to trace wires. You should go either directly up or down or left or right from where the wires go in, then turn a right angle and run to where the wires come out again.

...if that makes sense.
  Quote
Old 11-03-2005, 11:34 AM   #7
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Thanks for your advice,

The cables that are running diagonally are only the singnal cables, Power cables are running as they should, Straight up in separate conduit with capping protecting them from anyone drilling into them.
I was going to run the signal cables diagonally because it would be easier ti pull the cables though or to add new ones, I was also going to draw a plan up and inform any future occupant of where the cables run, do you think this is acceptable, I think the cables I have are not long enough for the other way. I may also remove the cables when we move.

Dann
Attached Files
File Type: doc Doc1.doc (23.5 KB, 83 views)
  Quote
Old 11-03-2005, 11:55 AM   #8
Member
Join Date: Apr 2003
Location: Norwich, UK.
Experience Points:
5,512, Level: 17
Points: 5,512, Level: 17 Points: 5,512, Level: 17 Points: 5,512, Level: 17
Activity: 1.4%
Activity: 1.4% Activity: 1.4% Activity: 1.4%
Thanks: Gave 0, Got 3
Posts: 446
Its mainly to protect against people accidentally drilling through power cables so you should be OK.

If you put anything in writing or draw up a plan to give to the next owners, make sure you mention that you did these mods before 2005 because otherwise you might compromise yourself under the new rediculous laws banning DIY electrics.
  Quote
Old 11-03-2005, 12:25 PM   #9
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
The power cable is just for the TV & I wll be using the original that came with the TV, This cable will pass through a Flex outlet, to connect to a socket, Because its the original I will be removing it when we move.

I am aware about the changes in the IEE Regs, & have the listed changes at work, I will double check but I think adding additional socket does not need certification as long as it is not in the kitchen or bathroom, I work with a few sparkies so I can get their advice if needed.

Basically most of the work will be removed when we go unless the next buyers request that it stays.

As long as 125mm x 40mm channel is ok i will start this weekend.

Thanks for all the advice

Dann
  Quote
Old 11-03-2005, 10:39 PM   #10
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,161, Level: 38
Points: 25,161, Level: 38 Points: 25,161, Level: 38 Points: 25,161, Level: 38
Activity: 34.1%
Activity: 34.1% Activity: 34.1% Activity: 34.1%
Thanks: Gave 2,331, Got 4,980
Posts: 21,265
125mm = 5 inches (or thereabouts), 40x40x125mm sounds like a cutout for a double socket patress box not a channel up the wall to pull cables through, are you sure you didn't mean 125cm for the length of the channel (ie about 4 feet). I'd definately be reticent about cutting a 40x40mm channel for 125 cm diagonally across a structural wall. Of course if you meant 125mm ignore what i just said.

Dave
  Quote
Old 12-03-2005, 3:36 PM   #11
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Hi Regmarch,
thanks fro spotting the mistake, I did mean 125cm. Do you think this would be a problem then?
  Quote
Old 12-03-2005, 4:04 PM   #12
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Just to add from the previous post.
Now that I have posted the correct measurments for the channel (125cm x 40mm x 40mm). SORRY EVERYONE.

If this is now thought of too deep, How deep do you recommend I go? I was hoping to be able to remove the cables by putting them In this 32mm Pipe, but If this is too deep I may as well cut a smaller channel & leave them I there.

what do you think?
  Quote
Old 12-03-2005, 4:38 PM   #13
Member
 
surrey lad's Avatar
Join Date: Dec 2002
Location: Epsom Downs
Experience Points:
4,359, Level: 15
Points: 4,359, Level: 15 Points: 4,359, Level: 15 Points: 4,359, Level: 15
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 12, Got 18
Posts: 626
Whats the wall made from and how thick is it?
  Quote
Old 12-03-2005, 4:48 PM   #14
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
The wall is 130mm thick & I think it is solid brick, Built in 1967 if that helps.

Looking at it again I think I have a better way of routing the pipe:

1 20mm Dia conduit for the power cable running striaght up for 900mm, 25mm deep.
1 35mm Dia Waste pipe for the rest of the cables running striaght up for 900mm, 40mm deep.

These channels would be running 20mm apart & both will have switch boxes at either end.

Sorry to keep changing the original question.

What do you think?
Attached Thumbnails
Chasing Walls-wall.bmp  

Last edited by dann; 12-03-2005 at 5:22 PM.
  Quote
Old 12-03-2005, 7:43 PM   #15
Member
Join Date: Nov 2002
Location: Birmingham, UK
Experience Points:
5,480, Level: 17
Points: 5,480, Level: 17 Points: 5,480, Level: 17 Points: 5,480, Level: 17
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 7, Got 15
Posts: 634
At 130mm thick, your wall is likely to be a 100 or 110 wide brick, with plaster each side.

IIRC, recommended chases are max 1/5 (ie 20mm) of the structural wall (ie brick). But it does depend on the location of the chase and if the wall is loadbearing.

32 conduit seems too wide for this purpose. Can't you use 20 or 25mm - eg standard plastic overflow pipe?
  Quote
Old 12-03-2005, 9:28 PM   #16
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
Hi woody, thanks for your reply, I could use 20mm conduit but will not be able to remove the cables unless I run 3 or more lengths, (which is probably worse than running 1 32mm one.

Thanks for your help, will have to bury them in for good I think, when all bunch togehter they are 25mm Dia ( not including the AC Supply).

Bearing in mind these will only be signal cables, Are they any restrictions on running these outside conduit?

thanks for your help
  Quote
Old 12-03-2005, 11:05 PM   #17
Member
Join Date: Nov 2002
Location: Birmingham, UK
Experience Points:
5,480, Level: 17
Points: 5,480, Level: 17 Points: 5,480, Level: 17 Points: 5,480, Level: 17
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 7, Got 15
Posts: 634
Conduit is only used domestically to faciliate easy cable installation and subsequent replacement. If these cables are to be permanent, then I cant see why you should not just gouge the plaster.

Power cable should run vertically or horizontally from wall outlets to aid tracing them. I am not too sure on running your A/c cable next to signal cables though as this may cause some interferance.
  Quote
Old 12-03-2005, 11:32 PM   #18
Member
Join Date: Aug 2003
Experience Points:
3,826, Level: 14
Points: 3,826, Level: 14 Points: 3,826, Level: 14 Points: 3,826, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 2
Posts: 134
I will be running the AC supply vertically only, same as the signal cables but will be at least 25mm apart in a separate channel, So there will be 2 25mm channels now, due to the info you have given me.

Does this sound OK?

Thanks alot for your help, Do you think that the majority of people with plasmas have buried permantly, Or ignore regulations?

Regards

Dan
  Quote
Post Reply



Thread information and display options
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off