Originally Posted by fredd500 The main difference is that the outputs on a UPS are indirectly powered - i.e. the incoming power charges a battery and the battery powers an inverter which then feeds the output. |
sorry, but that is actually incorrect.
The inverter is always powered via the mains. The battery source will only actually kick in if the voltage is out of tollerance or completely missing.
That is of course providing we're talking about an 'online' UPS.
The mains goes in via a rectifier, to convert to DC, then the filtering is done and then through the inverter back to AC and out to load.
This is also known as 'double conversion'. This means that the the output is voltage and frequency independant from the input.... resulting in Sinewave output.
Battery comes in instantly, no switchover time, by using ohms law.
If you like, the battery is ready, waiting, but the DC voltage is slightly higher than that of the one supplied via the rectifier, so the inverter will take the lower voltage (the easiest to get). When this fails, the only voltage left is that of the battery.
however, most UPS at the lower price range will be 'line-interactive'.
This is when the mains goes into the UPS, but stays as AC voltage into a AVS (automatic voltage stabiliser) and then out to the load.
The battery switches in if power is lost/voltage falls out of range etc, but has a few milisecond switch over time which can be picked up by some sensitive equipment.
HTH