Help! Lighting problem...

Hi all,

Got a bit of a problem with the lighting in my living room. I think it's just a basic electrical problem, hope someone can help.

Basically I have a lighting unit on the ceiling with four 50W halogen lamps. There is twin switch setup, with an on/off switch at one end of the room, and a dimmer switch at the other end of the room. This has been working perfectly for the last few months, with the dimmer providing the 'mood' lighting for watching movies, snogging the missus, etc.

A few weeks ago, I switched the lights on and one of the Halogen bulbs blew. The lights went out in the entire flat. Put in some new fuse wire in the fusebox, lighting comes back on. In the living room, 3 of the halogen lights are on full brightness, one is dead. The on/off switch works, the dimmer switch does NOT work - It will push on/off but the lights will not dim when turning the knob. Replaced dead bulb with new one. Dimmer switch still not working.

Concluded that dimmer switch must have blown - so, went out to B&Q, bought new dimmer switch (it is rated at 450W). Cost £20 (bloody expensive). Fitted new switch, all works perfectly - back to normal.

However, last weekend it's happened AGAIN. Exactly the same - another bulb in the lighting unit has blown, main lighting fuse has blown, dimmer switch blown. I don't want to spend £20 on a new dimmer every time a bulb blows!!

Any ideas what is causing the dimmer switch to blow, and how can I protect it? Do I need a dimmer with a higher power rating? Help....!

Cheers,
Mat
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 9:35 AM   #2 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Isn't there ANYONE here who might have some suggestions?
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 12:56 PM   #3 (permalink)
Member
Join Date: Dec 2002
Location: West Midlands
Posts: 47
iTrader: (0)
Thanks: Gave 1, Got 1
Think I have heard of this happening before. When the lamp blows it takes out dimmer, hence dimmers have to be derated. But if your dimmer is 450w and lights are 200w this should be ok IMO. I,m no electrician but but if you try the Screwfix forum you should get a more qualified answer to your problem.

http://www.screwfix.com/talk/index.j...orums&ts=33646

Good luck, Andy
andybed is offline  
Reply With Quote
Old 21-12-2004, 1:04 PM   #4 (permalink)
Senior Member
Join Date: Jan 2003
Location: New Crobuzon
Posts: 1,706
iTrader: (18)
Thanks: Gave 4, Got 43
Are the halogen lights Mains or Low voltage. I think with the low voltage ones you have to make sure the dimmer can handle the transformer for the lights or it will over heat and go pop.
__________________
Mat
avanzato is offline  
Reply With Quote
Old 21-12-2004, 1:17 PM   #5 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Quote:
Originally Posted by avanzato
Are the halogen lights Mains or Low voltage. I think with the low voltage ones you have to make sure the dimmer can handle the transformer for the lights or it will over heat and go pop.
This is unit I have, here.

These are 50W bulbs, I don't think they are low-voltage, I don't recall seeing a transformer in the unit. It's designed to directly replace a normal old-fashioned ceiling light, which is what I have done. The dimmer failure only occurs when one of the bulbs blows.

Mat
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 1:18 PM   #6 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Quote:
Originally Posted by andybed
Think I have heard of this happening before. When the lamp blows it takes out dimmer, hence dimmers have to be derated. But if your dimmer is 450w and lights are 200w this should be ok IMO. I,m no electrician but but if you try the Screwfix forum you should get a more qualified answer to your problem.

http://www.screwfix.com/talk/index.j...orums&ts=33646

Good luck, Andy
Thanks, I'll check it out.

Cheers,
Mat
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 2:26 PM   #7 (permalink)
Senior Member
Join Date: Jan 2003
Location: New Crobuzon
Posts: 1,706
iTrader: (18)
Thanks: Gave 4, Got 43
The John Lewis description says High spot bulbs which should mean they're 230v mains, GU10 or GZ10 is that right? What brand is the Dimmer switch and how is it wired, 2 way I assume.
__________________
Mat
avanzato is offline  
Reply With Quote
Old 21-12-2004, 2:37 PM   #8 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Yes I am pretty sure they're 230v or 240v - this sounds familiar as I was out buying spare bulbs a few weeks ago.

Yes, the dimmer is wired 2-way. I'll try and find a linky to the dimmer specs...
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 2:53 PM   #9 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
here you go:
http://www.tlc-direct.co.uk/Technica...lus_Dimmer.pdf

the model that I have is K1535 WHI - 1 gang, 2-way single dimmer switch, 60-450W.
dvdsubtitles is offline  
Reply With Quote
Old 21-12-2004, 3:15 PM   #10 (permalink)
Member
Join Date: Dec 2002
Location: West Midlands
Posts: 47
iTrader: (0)
Thanks: Gave 1, Got 1
From the spec sheet for your dimmer K1535 WHI which is a 'standard"sdimmer it states that its "only suitable for normal tungsten filament lamps with internal fuses", so if this is your dimmer its looks like it will not work with your light fitting and halogens.

Andy
andybed is offline  
Reply With Quote
Old 21-12-2004, 3:25 PM   #11 (permalink)
Member
Join Date: Dec 2002
Location: West Midlands
Posts: 47
iTrader: (0)
Thanks: Gave 1, Got 1
It also states in the spec sheet that the Intelligent dimmer has 'soft start' which is beneficial with mains voltage halogens due to the high inrush current at switch on. Did your faults occur when you first switched on the lights?. If so, its probably the intelligent dimmer that you need.

Andy
andybed is offline  
Reply With Quote
Old 21-12-2004, 3:34 PM   #12 (permalink)
Senior Member
Join Date: Jan 2003
Location: New Crobuzon
Posts: 1,706
iTrader: (18)
Thanks: Gave 4, Got 43
Yes I would agree as the text for the 'Intelligent Dimmer' on that MK info sheet says it is suitable for mains Halogen that it'll be OK for you. I would guess that the standard dimmer you have is going into 'Over Load protection' Mode 4 and shutting down as soon as the bulb goes. BTW is there a reset switch on the dimmer at all?

It is also just worth checking the wiring is done as per the diagram on that sheet for 2 way switching when you replace the switch.
__________________
Mat
avanzato is offline  
Reply With Quote
Old 21-12-2004, 10:12 PM   #13 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Quote:
Originally Posted by avanzato
Yes I would agree as the text for the 'Intelligent Dimmer' on that MK info sheet says it is suitable for mains Halogen that it'll be OK for you.
I can't find this - I can only find a bit that says it is suitable for "low voltage Halogen bulbs". The bulbs I use are labelled GU10+C 240V 50W - these are not "low voltage" are they? I'm pretty sure there are no transformers within the lighting unit.


Quote:
BTW is there a reset switch on the dimmer at all?
No, there definitely isn't.

We're getting there....
dvdsubtitles is offline  
Reply With Quote
Old 22-12-2004, 12:12 AM   #14 (permalink)
Senior Member
Join Date: Jan 2003
Location: New Crobuzon
Posts: 1,706
iTrader: (18)
Thanks: Gave 4, Got 43
GU10 are mains voltage and don't use a transformer so you're OK there. I'm inferring that as the specs for the intelligent dimmer have 'soft start' and that feature is beneficial to Mains Halogen use. Then the intelligent dimmer is in fact suitable to be used with mains halogen lights. Reading the sheet again it looks like the 4 modes of shut down also apply to the intelligent dimmer not the standard one as I first thought. The standard one just has a thermal cutout safety device.

I also found this on interDIY that explains why a bulb going pop trips the circuit breaker.
__________________
Mat
avanzato is offline  
Reply With Quote
Old 22-12-2004, 9:26 AM   #15 (permalink)
Member
Join Date: Aug 2004
Location: London
Posts: 216
iTrader: (0)
Thanks: Gave 1, Got 0
Quote:
Originally Posted by avanzato
GU10 are mains voltage and don't use a transformer so you're OK there. I'm inferring that as the specs for the intelligent dimmer have 'soft start' and that feature is beneficial to Mains Halogen use. Then the intelligent dimmer is in fact suitable to be used with mains halogen lights. Reading the sheet again it looks like the 4 modes of shut down also apply to the intelligent dimmer not the standard one as I first thought. The standard one just has a thermal cutout safety device.

I also found this on interDIY that explains why a bulb going pop trips the circuit breaker.
Right, yes I've managed to find the manufacturer's website and it does mention specifically on there that the intelligent dimmers are suitable for mains voltage halogens, so you were right.

However, getting one of these dimmers might be a bit of a palaver, so I'll call the manufacturers and find my nearest dealer.

I'm gonna do two things: get this new dimmer, and also get a plug-in circuit breaker to replace the lighting fuse wire in my current fuse box.

Thanks for all your help, much appreciated!!

Cheers,
Mat
dvdsubtitles is offline  
Reply With Quote

Bookmarks

Tags
lighting, problem


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT. The time now is 3:15 PM.

AV ForumsOptimised for Firefox.
RSS Feed
AVForums.com is owned and operated by M2N Limited.
Copyright © 2000-2008 M2N E. & O. E.
Global Gold
Web Hosting