hi all
couple of questions for you
im putting some downlights in the frontroom and bedroom shortly as im building a new ceiling on the existing and we will be putting downlights in
6 in the livingroom and 4 in the bedroom ,but thats here nor there
i want to use some lutron dimmers so im making sure i get the right lights
the gu10 seem popular and there are fire rated versions as is here Fire Rated Mains Downlights GU10 Halogen
will these do the job?
as its going in the ceiling which will be packed out with insulation of some sort will these type be ok ? ,or which will?
and will they work with the lutron dimmers?
as you can see im pretty confused so any advice is more than welcome

many thanks
leigh
  Quote
Old 11-02-2009, 11:25 PM   #2
Member
Join Date: Jun 2008
Location: Sheffield
Experience Points:
1,678, Level: 9
Points: 1,678, Level: 9 Points: 1,678, Level: 9 Points: 1,678, Level: 9
Activity: 1.0%
Activity: 1.0% Activity: 1.0% Activity: 1.0%
Thanks: Gave 23, Got 38
Posts: 491
Re: downlight advice please

Which type/family of Lutron dimmer do you wish to use? I'm going to make an assumption it's a Rania type, in which case it should be OK.

These lamp fittings are OK, but can be had from Screwfix in a ten pack for maybe a bit less. However, if you are doing a new installation you should think about adding transformers and using low voltage light fittings, they will use less energy and the lamps last longer. Also, I'm pretty sure that Part P regulations come into play when installing new lighting, so I think you need to get your local building control officer or qualified electrician involved.
  Quote
Old 12-02-2009, 8:56 PM   #3
Senior Member
Join Date: Jun 2003
Location: watford
Experience Points:
5,391, Level: 17
Points: 5,391, Level: 17 Points: 5,391, Level: 17 Points: 5,391, Level: 17
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 49, Got 48
Posts: 1,448
Re: downlight advice please

hi thanks for the reply
your right regarding the lutron ie the rania
happy to go with the low voltage/transformer option
so i take it they would be compatible with the rania? as that was my only worry
and i know plenty of sparkies so thats no problem

cheers
leigh
  Quote
Old 13-02-2009, 4:51 PM   #4
Member
Join Date: Jun 2008
Location: Sheffield
Experience Points:
1,678, Level: 9
Points: 1,678, Level: 9 Points: 1,678, Level: 9 Points: 1,678, Level: 9
Activity: 1.0%
Activity: 1.0% Activity: 1.0% Activity: 1.0%
Thanks: Gave 23, Got 38
Posts: 491
Re: downlight advice please

I use a Rania dimmer unit with a Halolite HS60 60va prewired transformer, they are about £9 each but they do the job. I used one 60va transformer for each lamp, as when I first put them in my wife was concerned certain areas were not bright enough, and I did not want to be upgrading transformers buried in the ceiling.

If you want something a bit more robust, Lutron make their own transformers which are compatible with all their products, these are around £12 + vat each.

Its a little more outlay to begin with, but they pay for themselves pretty quickly in reduced electricity bills.
  Quote
Thanks from:
leighprice23 (13-02-2009)
Old 13-02-2009, 6:05 PM   #5
Senior Member
Join Date: Jun 2003
Location: watford
Experience Points:
5,391, Level: 17
Points: 5,391, Level: 17 Points: 5,391, Level: 17 Points: 5,391, Level: 17
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 49, Got 48
Posts: 1,448
Re: downlight advice please

thanks again i shall have a look online
one more thing though
i take it the low voltage ones stay pretty cool?
ie they will be ok in a ceiling padded out with insulation etc or do they need breathing space ?
cheers

leigh
  Quote
Old 13-02-2009, 8:05 PM   #6
Member
Join Date: Jun 2008
Location: Sheffield
Experience Points:
1,678, Level: 9
Points: 1,678, Level: 9 Points: 1,678, Level: 9 Points: 1,678, Level: 9
Activity: 1.0%
Activity: 1.0% Activity: 1.0% Activity: 1.0%
Thanks: Gave 23, Got 38
Posts: 491
Re: downlight advice please

All the units on sale in the EU are supposedly rated to be used in ceiling voids and on top of insulation, some can even be used on sensitive surfaces, so you can place on or near to surfaces with risk of overheating or fire. The LV transformers in my house are just placed on top of the insulation material.

The lamps get hot (as do mains voltage units) so you need to place a hood around the fitting to comply with fire ratings or use a fire rated light unit.
  Quote
Thanks from:
leighprice23 (13-02-2009)
Old 13-02-2009, 8:19 PM   #7
Member
Join Date: Jan 2005
Location: Milton Keynes
Experience Points:
8,104, Level: 21
Points: 8,104, Level: 21 Points: 8,104, Level: 21 Points: 8,104, Level: 21
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 25, Got 91
Posts: 921
Re: downlight advice please

I used these loftcaps on all my downlighters on the top floor (i.e. the ones that are mounted into the ceiling below the loft). They allow you to re-lay the insulation over the top of the light without risk of overheating. You shouldnt lay insulation over the top of lights even if fire rated as they have holes in the back to allow heat out. I used the loftcaps with fire rated lights aswell but this isnt essential.

Fire Vapour & Thermal Seal Loft Cap

Hope this helps
  Quote
Thanks from:
dalethecaptain (13-02-2009), leighprice23 (15-02-2009)
Old 15-02-2009, 6:35 PM   #8
New Member
Join Date: Apr 2008
Experience Points:
1,402, Level: 8
Points: 1,402, Level: 8 Points: 1,402, Level: 8 Points: 1,402, Level: 8
Activity: 0.3%
Activity: 0.3% Activity: 0.3% Activity: 0.3%
Thanks: Gave 0, Got 5
Posts: 28
Re: downlight advice please

I would recommend Low Voltage everytime over GU10's. The quality of light is much greater than GU10's, therefore much more energy effiecient. a lot of the GU10 energy is consumed into heat. you can really notice the heat off of a GU10, and heat is just a loss of energy!

The best transformer on the market are Mode Liighting ET-C's. They are silent and can be controlled by trailing or leading edge, and really are fit and forget. they are more expensive at £13.00 each, but were the recommended transformer from Lutron, before they decided to make their own!
  Quote
Thanks from:
leighprice23 (17-02-2009)
Old 18-02-2009, 10:58 AM   #9
Member
 
MarkP80's Avatar
Join Date: Jan 2005
Location: Aberdoon!
Experience Points:
6,231, Level: 18
Points: 6,231, Level: 18 Points: 6,231, Level: 18 Points: 6,231, Level: 18
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 112, Got 99
Posts: 915
Re: downlight advice please

Quote:
I would recommend Low Voltage everytime over GU10's. The quality of light is much greater than GU10's, therefore much more energy effiecient. a lot of the GU10 energy is consumed into heat. you can really notice the heat off of a GU10, and heat is just a loss of energy!
- you still get a lot of heat passing back from a low voltage halogen though, that's for sure.

Quote:
I used these loftcaps on all my downlighters on the top floor (i.e. the ones that are mounted into the ceiling below the loft).
Fire Vapour & Thermal Seal Loft Cap
- Do you use these with LV downlights? If so, where did you put the transformer? In the past, I have fitted individual transformers to each downlight, slimline units through the same hole, so they can be slid back out if they need to be changed. What did you do here? Can the transformer go under tha cap too? - Would it not get too hot? - Or have you put the trasnfromer outside the cap, and assumed access from above (in the loftspace). I ask because I've been pondering this issue for some time, as I will be doing some work in upstairs rooms before too long, and want to get the insulation right, without the fire risk!

Regards,
MarkP
  Quote
Old 18-02-2009, 5:51 PM   #10
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

The best thing to use is a fire rated downlighter - do not purchase from Screwfix or the like, go to a proper electrical wholesaler. Companies such as City Electrical Factors and Edmunson's are nationwide.

I prefer the Click brand, but many do get on with the JCC ones.

Ensure that you buy decent quality lamps and do not use the rubbish ones they supply with them - GE are a good example, as are Sylvania.

There is no energy saving in using ELV (12V) lamps over mains voltage ones, anyone who assumes as such is sadly misinformed. There is something to be said for a slightly longer life expectancy when ELV lamps and fittings are used, but for me the difference isn't worth the extra cost of decent transformers.

The heat output from any standard downlight is extreme, hence the need for a fire rated fitting (there are also acoustic considerations, as per part E of the building regs). You need to leave a 50mm gap around all of the fitting, in every direction.

You may wish to consider buying compact fluorescent lamps (these do come in a GU10 form factor), as these will save you a fair old whack on the electric bill. They run at about 8W as opposed to 50W and have a similar light output.

As someone has mentioned, there are the Part P regs to consider, but these are only relevant if you are installing a complete new circuit. You still need to test anything you install (and I'm assuming a DIYer doesn't own the kit), so have a word with a friend electrician and he'll quickly do it and you can buy him a drink.
  Quote
Thanks from:
MarkP80 (19-02-2009)
Old 19-02-2009, 1:58 PM   #11
Member
 
MarkP80's Avatar
Join Date: Jan 2005
Location: Aberdoon!
Experience Points:
6,231, Level: 18
Points: 6,231, Level: 18 Points: 6,231, Level: 18 Points: 6,231, Level: 18
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 112, Got 99
Posts: 915
Re: downlight advice please

Been doing a bit more research on this. It seems your normal dichroic LV halogen bulbs aren't suitable for fire resistant fittings. These allow a lot of heat through the bulb back into the fitting. For fire resistant fittings you should use bulbs with an aluminium reflector according to this

I was wondering earlier about using the loftcap, and which side of it the transformer would go. Well, perhaps an alternative solution is to use a fire resistant fitting like this, then use something like this cover - this solves a couple of issues. It allows the air space to be maintained around the fitting while letting you put your loft insulation over the top, and also provides the space for you to poke that slimline transformer and JB through the hole when you install them. OK, not necessarily the cheapest solution, but certainly makes the installation simple and straightforward, does it not?

Cheers,
MarkP

Last edited by MarkP80; 19-02-2009 at 2:00 PM.
  Quote
Old 19-02-2009, 2:13 PM   #12
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

For clarification matters, LV is anything below 1000V AC and 1500V DC, so the lamps you're referring to are ELV.

Almost all lamps supplied by anywhere decent (not B&Q et al) have reflective inners, however the heat output through the rear is almost identical, so fire rated fittings are still required.

There is the option to fit fire hoods, or a fire blanket, but standard downlight fittings do not comply with Part E of the building regulations, therefore a fire rated fitting solves this issue.

When installing any electrical items the install must comply with Parts B, E, L, M and P of the building regulations (by law) and it is also strongly advised to comply with the BS7671 wiring regulations, although these are not mandatory.
  Quote
Old 19-02-2009, 3:16 PM   #13
Senior Member
Join Date: Jan 2005
Location: Scottish Borders
Experience Points:
5,329, Level: 17
Points: 5,329, Level: 17 Points: 5,329, Level: 17 Points: 5,329, Level: 17
Activity: 6.1%
Activity: 6.1% Activity: 6.1% Activity: 6.1%
Thanks: Gave 33, Got 203
Posts: 1,160
Re: downlight advice please

Quote:
Originally Posted by silver12 View Post
For clarification matters, LV is anything below 1000V AC and 1500V DC, so the lamps you're referring to are ELV.

Almost all lamps supplied by anywhere decent (not B&Q et al) have reflective inners, however the heat output through the rear is almost identical, so fire rated fittings are still required.

There is the option to fit fire hoods, or a fire blanket, but standard downlight fittings do not comply with Part E of the building regulations, therefore a fire rated fitting solves this issue.

When installing any electrical items the install must comply with Parts B, E, L, M and P of the building regulations (by law) and it is also strongly advised to comply with the BS7671 wiring regulations, although these are not mandatory.
Your comment about all lamps passing the same amount of heat back through their reflector and into the fitting/ceiling void is not correct. As MarkP80 has stated there are MR16 lamps with aluminium coatings which reflect most of the heat produced forward into the room and many (if not all) fire rated lv fittings require the use of this type of lamp. This is very different to standard MR16 lamps (sometimes called cool beam) which allow most of their heat (and a reasonable amount of light) to pass through the reflector and therefore not into the room. If the OP is in any doubt then they could look at the lighting packs sold by the likes of Aurora which have the fitting, transformer and correct lamp supplied together, this will ensure they are all compatible.
  Quote
Thanks from:
leighprice23 (19-02-2009)
Old 19-02-2009, 3:42 PM   #14
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

I said that anywhere decent selling lamps (either MR16 or GU10) provide reflective inners, these are almost identical to any supplied through TLC which claim any greater degree of reflectiveness or heat protection. If you measure the heat output through the rear of a lamp fitted with a reflective inner using a thermal imager you'll discover the difference is nowhere near enough to consider not using fire rated fittings (not that you suggested not to).

Aurora are a fairly decent brand of light fittings, and their fire rated fittings I personally think are one of the best.

If money is no object for the OP then LED fittings would be the best option, however cost is considerably higher.
  Quote
Old 20-02-2009, 7:00 AM   #15
Member
 
MarkP80's Avatar
Join Date: Jan 2005
Location: Aberdoon!
Experience Points:
6,231, Level: 18
Points: 6,231, Level: 18 Points: 6,231, Level: 18 Points: 6,231, Level: 18
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 112, Got 99
Posts: 915
Re: downlight advice please

Quote:
For clarification matters, LV is anything below 1000V AC and 1500V DC, so the lamps you're referring to are ELV.
- You're correct of course, but for most DIY'ers 230v is the maximum voltage we deal with.

Quote:
When installing any electrical items the install must comply with Parts B, E, L, M and P of the building regulations (by law) and it is also strongly advised to comply with the BS7671 wiring regulations, although these are not mandatory.
- but only if those regs apply. Part P doesn't necessarily, for example.

Quote:
If you measure the heat output through the rear of a lamp fitted with a reflective inner using a thermal imager you'll discover the difference is nowhere near enough to consider not using fire rated fittings (not that you suggested not to).
- Just to clarify, I certainly wasn't suggesting the use of non-fire resistant fittings, (as silver12 acknowledged), just noting that a fully enclosed fire resistant fitting is enclosed at the rear and so heat build up is retained, whereas a conventional fitting doesn't suffer from this. Clearly, it doesn't form a fire barrier either though....

As for the quality of the bulbs, I don't profess to be an expert, but it was my understanding that conventional dichroic halogen bulbs only reflect visible light frequencies, but allow non-visisible radiant heat to pass through, whereas bulbs with aluminium reflectors do not. Different types as opposed to different qualities?

Edit - quickly Googled - Glossary - gives a definition for aluminium reflector and dichroic.

MarkP

Last edited by MarkP80; 20-02-2009 at 7:10 AM.
  Quote
Old 20-02-2009, 10:44 AM   #16
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

I was letting people know it's ELV incase they need to know when buying certain items, although most people do seem to refer to it as LV.

Part P always applies, it just depends to what extent, and whether building control need to be notified of the work. The Part P document can be downloaded from the ODPM website, as can the other parts of the building regs.

The only place you'll be able to buy those rubbish lamps is places like B&Q, which is exactly why I always tell people to avoid them at all costs.
  Quote
Old 21-02-2009, 6:14 PM   #17
Zog Zog is offline
Member
 
Zog's Avatar
Join Date: Aug 2001
Location: Manchester
Experience Points:
6,436, Level: 19
Points: 6,436, Level: 19 Points: 6,436, Level: 19 Points: 6,436, Level: 19
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 3, Got 5
Posts: 404
Re: downlight advice please

OK.... my two-penneth worth.

12v over 240v everytime - light quality, lamp life and safety.

For bedrooms DON'T PUT THE FITTINGS DIRECTLY OVER THE BED.

Think about it. Do you really want to be looking directly into downlights while trying to relax ?

Put them around the bed, and preferably use directional luminaires that can be aimed at the wall.

This is with the possible exception of the wall directly opposite the window. If you light this too brightly then the neighbours will get a great view of whatever you might get up to in their...
  Quote
Old 21-02-2009, 6:40 PM   #18
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

Light quality is no better with an 12V lamp than it is with a 230V lamp.

Longer life lamps are now available in a GU10 form factor, ok you'll pay a slight premium for them but it's worth it.

There is no real safety benefit with ELV fittings. In a wet installation of course it's a neccessity, but when installed correctly a 230V is no more or less safe than a 12V one.

It is also worth noting that any ELV installation comes under the scope of notifiable work under Part P - not just in special locations but everywhere. If you were altering the lights in your bedroom using 230V fittings you could carry out the work yourself, using ELV ones you need to either get someone in, or notify BC and pay their exorbitant fees.
  Quote
Old 21-02-2009, 8:07 PM   #19
Senior Member
Join Date: Jan 2005
Location: Scottish Borders
Experience Points:
5,329, Level: 17
Points: 5,329, Level: 17 Points: 5,329, Level: 17 Points: 5,329, Level: 17
Activity: 6.1%
Activity: 6.1% Activity: 6.1% Activity: 6.1%
Thanks: Gave 33, Got 203
Posts: 1,160
Re: downlight advice please

Quote:
Originally Posted by silver12 View Post
Light quality is no better with an 12V lamp than it is with a 230V lamp.

Longer life lamps are now available in a GU10 form factor, ok you'll pay a slight premium for them but it's worth it.

There is no real safety benefit with ELV fittings. In a wet installation of course it's a neccessity, but when installed correctly a 230V is no more or less safe than a 12V one.

It is also worth noting that any ELV installation comes under the scope of notifiable work under Part P - not just in special locations but everywhere. If you were altering the lights in your bedroom using 230V fittings you could carry out the work yourself, using ELV ones you need to either get someone in, or notify BC and pay their exorbitant fees.
Cannot comment on Part P, I'm in Scotland and this does nor apply. It would seem odd that the regs would be different though as both need to be connected to mains at some point - GU10s directly and ELVs via transformers. As you can buy ELV fittings with the transformer pre-fitted/wired already then with these kinds of fittings there is no practical difference at all.

However their is a very marked difference in the light from a 230v GU10 and an 12v MR16 lamp, GU10s are still a very warm colour as opposed to the crisp white light from MR16s. It does not matter whether the GU10s are long-life, from major manufacturers or anything else, put them side by side (or even go from room to room with these different fittings) and you will see the difference. The major benefit of GU10s is the fact that the fitting is fully self-contained and prevents installers from mis-matching or improperly wiring up the transformers, but as I said above (sounding a bit like a stuck record now!!) you can but pre-wired kits that have the correct transformers and spec of cabling on the ELV side and thereby avoid the common pitfalls.

Finally there are long-life and more efficient/lower energy versions of both GU10 and MR16 although the MR16 can be had in slightly more efficient versions i.e. lower energy. These use a different gas in the lamp capsule and coatings on the reflector and emit more energy as visible light. For example a 30W MR16 has the same light pattern and output as a 50W conventional lamp, a 40% saving over standard but still fully dimmable, same quality of light and fit the standard fitting/transformer without any other changes. They are around 4x the cost of standard lamps but also last much longer.
  Quote
Old 21-02-2009, 8:15 PM   #20
Zog Zog is offline
Member
 
Zog's Avatar
Join Date: Aug 2001
Location: Manchester
Experience Points:
6,436, Level: 19
Points: 6,436, Level: 19 Points: 6,436, Level: 19 Points: 6,436, Level: 19
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 3, Got 5
Posts: 404
Re: downlight advice please

Quote:
Originally Posted by silver12 View Post
Light quality is no better with an 12V lamp than it is with a 230V lamp.

Longer life lamps are now available in a GU10 form factor, ok you'll pay a slight premium for them but it's worth it.

There is no real safety benefit with ELV fittings. In a wet installation of course it's a neccessity, but when installed correctly a 230V is no more or less safe than a 12V one.

It is also worth noting that any ELV installation comes under the scope of notifiable work under Part P - not just in special locations but everywhere. If you were altering the lights in your bedroom using 230V fittings you could carry out the work yourself, using ELV ones you need to either get someone in, or notify BC and pay their exorbitant fees.
Size of the capsule is far larger within a GU10 so the control of the light it emits is far poorer. This leads to very visible striatians, especially visible when used on walls, and inconsistancies between lamps of the same beam width.

Also as the 12v dichroic emits reduced amounts of red light, then the result is a crisper colour appearance.

Yes lamp lifes have improved, but they are still not the same as branded 12v, especially the 12,000 hr that are now on the market.

As for the Part P, I'm a designer/manufacturer, so I wouldn't comment. But I would ask how would the powers that be ever know ?
  Quote
Old 22-02-2009, 8:36 AM   #21
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

Quote:
Originally Posted by neilball View Post
Cannot comment on Part P, I'm in Scotland and this does nor apply. It would seem odd that the regs would be different though as both need to be connected to mains at some point - GU10s directly and ELVs via transformers. As you can buy ELV fittings with the transformer pre-fitted/wired already then with these kinds of fittings there is no practical difference at all.

However their is a very marked difference in the light from a 230v GU10 and an 12v MR16 lamp, GU10s are still a very warm colour as opposed to the crisp white light from MR16s. It does not matter whether the GU10s are long-life, from major manufacturers or anything else, put them side by side (or even go from room to room with these different fittings) and you will see the difference. The major benefit of GU10s is the fact that the fitting is fully self-contained and prevents installers from mis-matching or improperly wiring up the transformers, but as I said above (sounding a bit like a stuck record now!!) you can but pre-wired kits that have the correct transformers and spec of cabling on the ELV side and thereby avoid the common pitfalls.

Finally there are long-life and more efficient/lower energy versions of both GU10 and MR16 although the MR16 can be had in slightly more efficient versions i.e. lower energy. These use a different gas in the lamp capsule and coatings on the reflector and emit more energy as visible light. For example a 30W MR16 has the same light pattern and output as a 50W conventional lamp, a 40% saving over standard but still fully dimmable, same quality of light and fit the standard fitting/transformer without any other changes. They are around 4x the cost of standard lamps but also last much longer.
I think the Part P requirement has come in as a 'catch-all', because of the amount of bad DIYers out there. As is always the case in this country, it's police the many for the sake of the few.

You can buy GU10 lamps with just as good colour rendering now, without paying too much more. Companies like Osram and GE have spent a lot of time and money investing in this problem, which I agree at the outset of downlight installation was massive. These days the difference is minimal, and for my mind the benefit is not worth the extra hassle and cost an ELV install represents.

For what it's worth, I would never recommend fitting GU10 230V downlighters anyway, I would try and persuade anyway into an LED route, or at the very least use CFL lamps.
  Quote
Old 22-02-2009, 8:40 AM   #22
Member
Join Date: Feb 2009
Experience Points:
1,653, Level: 9
Points: 1,653, Level: 9 Points: 1,653, Level: 9 Points: 1,653, Level: 9
Activity: 2.7%
Activity: 2.7% Activity: 2.7% Activity: 2.7%
Thanks: Gave 7, Got 22
Posts: 430
Re: downlight advice please

Quote:
Originally Posted by Zog View Post
Size of the capsule is far larger within a GU10 so the control of the light it emits is far poorer. This leads to very visible striatians, especially visible when used on walls, and inconsistancies between lamps of the same beam width.

Also as the 12v dichroic emits reduced amounts of red light, then the result is a crisper colour appearance.

Yes lamp lifes have improved, but they are still not the same as branded 12v, especially the 12,000 hr that are now on the market.

As for the Part P, I'm a designer/manufacturer, so I wouldn't comment. But I would ask how would the powers that be ever know ?
Again, that was very much the case when they were first being made, but the problem has been addressed, and for my mind, solved. I think the problem lies in people buying their lamps/fittings at places like B&Q/Screwfix which sell the lowest of the low.

You can buy 10k hour GU10 lamps, that's not a bad difference! And besides, if one were too bothered about lamp life, one would go down the LED route - you can get 50k hour lamp life!

They might never find out, however it is possible that at the stage of selling a house (or even if your home insurance company suddenly asks for it, something which I think will eventually happen for all homeowners) and you have a PIR (Periodic Inspection Report) carried out, the tester may notice and ask to see the installation certificate.

Not that I wish to advocate breaking the law, but I do feel that a competent DIYer should be able to do as they wish. The problem is that most DIYers don't own the test equipment they need to test the installation.
  Quote
Old 09-06-2009, 3:15 PM   #23
Mobydick
Guest
Posts: n/a
Re: downlight advice please

There are some good CFL alternatives to halogen - Megaman and Aurora Lighting both have good products. Aurora have their 'Luna' range of CFL energy efficient lamps to fit with their fire rated Downlights.

I have installed their AU-DLM841 Fire rated downlights with the AU-GUF4011/30 lamps and they give a better light output than the GU10 downlights they replaced. Also the the lamps give 40 Lumens per Watt so would help with the L1 building regs.
  Quote
Old 11-06-2009, 1:46 PM   #24
New Member
Join Date: Apr 2008
Experience Points:
1,402, Level: 8
Points: 1,402, Level: 8 Points: 1,402, Level: 8 Points: 1,402, Level: 8
Activity: 0.3%
Activity: 0.3% Activity: 0.3% Activity: 0.3%
Thanks: Gave 0, Got 5
Posts: 28
Re: downlight advice please

Quote:
Originally Posted by MarkP80 View Post
- you still get a lot of heat passing back from a low voltage halogen though, that's for sure.
yes, you do still get heat, but nothing near a GU10. 240V in a small housing like a GU10 is a bad mix. when a GU10 blows, it will take out you fuse because of the bulbs construction, the filament shorts out! you can buy GU10's with the fuse in-built, but still the light quality is not as good.

A 12V MR16 will last longer and give out better light, with less heat, therefore making it a more energy efficient bulb.

CFL MR16 sized units are good energy savers, but dimming them is not good
  Quote
Post Reply



Thread information and display options
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off