replacing a faulty room thermostat

Hi all,

would be grateful for some advice. Our room thermostat is faulty and I have replaced it with a new one. There are 3 wires, red, yellow & blue although the blue is cut short and wasnt connected to anything in the old thermostat.

There are 3 terminals on the thermostat and Ive connected the yellow to 'on', the red to whats only numbered as '2' and no cable in the terminal marked 'off'.

When I put the power back on after connecting, the boiler starts but the thermostat doesnt switch it off.. Ive tried other combinations with the cables but it seems to be either always on or not at all.

Should I be using the blue (neutral I guess) in the terminal marked 'off'?

any advice much appreciated.

Last edited by dmx005; 06-09-2008 at 11:10 AM.
  Quote
Old 06-09-2008, 11:10 AM   #2
Member
Join Date: Mar 2005
Experience Points:
2,757, Level: 12
Points: 2,757, Level: 12 Points: 2,757, Level: 12 Points: 2,757, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 4, Got 33
Posts: 344
Re: replacing a faulty room thermostat

No.
The nuetral is there for a pre heating resistor that some themostats use to even out large swings in temp.
  Quote
Old 06-09-2008, 11:12 AM   #3
Member
 
dmx005's Avatar
Join Date: Jul 2005
Location: Leeds
Experience Points:
3,902, Level: 14
Points: 3,902, Level: 14 Points: 3,902, Level: 14 Points: 3,902, Level: 14
Activity: 0.4%
Activity: 0.4% Activity: 0.4% Activity: 0.4%
Thanks: Gave 67, Got 20
Posts: 597
Re: replacing a faulty room thermostat

Quote:
Originally Posted by hufartd View Post
No.
The nuetral is there for a pre heating resistor that some themostats use to even out large swings in temp.
thanks.. so any ideas why the boiler is always on regardless on whether the thermostat dial is switched on of off..? There are not many combinations - Ive only got 2 cables and 3 terminals to play with!

diagram & my wiring attached..
Attached Images
File Type: jpg wiring diagram.jpg (38.1 KB, 1923 views)
File Type: jpg wiring.jpg (53.5 KB, 961 views)

Last edited by dmx005; 06-09-2008 at 12:44 PM.
  Quote
Old 06-09-2008, 2:15 PM   #4
Senior Member
Join Date: Jan 2005
Location: Scottish Borders
Experience Points:
5,329, Level: 17
Points: 5,329, Level: 17 Points: 5,329, Level: 17 Points: 5,329, Level: 17
Activity: 6.1%
Activity: 6.1% Activity: 6.1% Activity: 6.1%
Thanks: Gave 33, Got 203
Posts: 1,160
Re: replacing a faulty room thermostat

The wiring diagram shows that terminal 1 should be your live feed from the boiler/boiler control circuit and that terminal 2 is the switched live back to whatever is to be controlled. Depending on your current wiring arrangments the stat will be wired in series with your central heating timeclock/programmer and then feeds back to the boiler directly (if it's a combi) or to a 2-port or 3-port zone valve (standard S-plan or Y-plan arrangement common in most houses). In the s-plan/y-plan arrangements the boiler is activated by a switch in the valve actuator so there could be 2 problems if the heating is not switching off - the new stat could be faulty or the end switch of the actuator has failed and is constantly supplying a feed to the boiler regardless of whether the valve is open or not.
  Quote
Old 08-09-2008, 9:42 PM   #5
New Member
Join Date: Mar 2008
Experience Points:
2,577, Level: 11
Points: 2,577, Level: 11 Points: 2,577, Level: 11 Points: 2,577, Level: 11
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 0, Got 1
Posts: 10
Re: replacing a faulty room thermostat

If you turn the dial to the lowest temp and slowly increase it do you hear / feel a click ? the switch breaking ? could be that the stat isn't switching properly ? do you have a meter ?? so you can test the switching of the stat ?
  Quote
Old 09-09-2008, 10:42 AM   #6
Member
Join Date: Jun 2002
Location: Surrey
Experience Points:
4,382, Level: 15
Points: 4,382, Level: 15 Points: 4,382, Level: 15 Points: 4,382, Level: 15
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 1, Got 14
Posts: 758
Re: replacing a faulty room thermostat

The thing to remember is that the thermostat is simply a switch. To find out where the fault lies try this:
Remember to turn off the power before making or breaking connections - potential 240V on these wires

Disconnect the thermostat and leave the 2 wires apart. Turn on the heating (making sure that the hot water is turned off). Note what happens.
Turn the power off - connect the 2 wires together (using abit of choc block or similiar) and turn it back on. Note what happens.

If the same thing happened in both states then the fault is not with the thermostat
If it did turn off and then on in both cases then you now know whether the boiler expects a normally open (NO) or a normally closed (NC) connection. Work out which connection is which on the thermostat and Bob's your auntie
Make any sense ??
  Quote
Post Reply



Thread information and display options
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off