Yet another boiler question.

My boiler is a Main combi 24 HE. The manual says Potterton owned by Baxi.

Over the last 2 weeks the heating pressure gauge was low, so topped it back to 1BAR. Next day down to a half, did the same several times but the same thing kept happening. Bled the rads, some air but not a lot, topped up again but same thing happened so called engineer.

He said i have a leak somewhere on the heating system as that's why the pressure gauge keeps falling. But after a few days watching it i'm not so sure.

The pressure gauge seems to have a life of it's own. One minute on 0, next 1 and anywhere in between no matter if the boilers going or not.Even at zero the boiler is working fine. Yesterday i turned the heating side off and it still read differently every time i looked at it.

Something else i noticed is that when a tap is turned on the gauge shoots up but about a BAR and dropped as soon as it was turned off. I didn't think sealed systems were meant to do that.

The boilers 2 and a half years old and was serviced in October.

I don't want to have to take up laminate floor unless it's realy neccessary.

Any ideas.

Thanks.
  Quote
Old 18-02-2009, 4:45 PM   #2
Member
Join Date: Feb 2006
Experience Points:
3,591, Level: 14
Points: 3,591, Level: 14 Points: 3,591, Level: 14 Points: 3,591, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 4, Got 33
Posts: 536
Re: Yet another boiler question.

May be due to lack of pressure in the expansion vessel. These do occasionally require topping up with air. As the water in the system heats it expands into the expansion vessel thus maintaining a constant pressure in the system. If the pressure gets too high it opens the pressure relief valve and some water escapes. Then when the water cools down again the pressure drops. You top it up and the cycle is repeated.

I would also consult the experts on DIY - Home Improvement - Do It Yourself
  Quote
Thanks from:
KoThreads (19-02-2009)
Old 18-02-2009, 7:08 PM   #3
Senior Member
Join Date: Jan 2005
Experience Points:
8,744, Level: 22
Points: 8,744, Level: 22 Points: 8,744, Level: 22 Points: 8,744, Level: 22
Activity: 1.9%
Activity: 1.9% Activity: 1.9% Activity: 1.9%
Thanks: Gave 311, Got 135
Posts: 2,766
Re: Yet another boiler question.

Isn't the expansion vessel part of the system i'm refilling to top up the CH pressure?
  Quote
Old 19-02-2009, 10:08 AM   #4
Member
Join Date: Feb 2006
Experience Points:
3,591, Level: 14
Points: 3,591, Level: 14 Points: 3,591, Level: 14 Points: 3,591, Level: 14
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 4, Got 33
Posts: 536
Re: Yet another boiler question.

The expansion vessel is split into two sections seperated by a rubber membrane with air in one side and water in the other. With the boiler drained of water the air pressure is set at a specific level. When the boiler water heats up it expands and presses against the membrane and compresses the air. This allows water to expand without increasing pressure. As the water cools, it contracts and the air expands to maintain the correct pressure in he system.

If both air and water pressure are set correctly, then a fairly constant pressure should be maintained throughout the heating/cooling cycles.

Occasionally the membrane can be pierced allowing water into the air chamber, which unfortunately means a replacment expansion vessel.
  Quote
Old 19-02-2009, 11:54 AM   #5
Senior Member
 
dazza1011's Avatar
Join Date: Jun 2006
Location: Sheffield
Experience Points:
2,340, Level: 11
Points: 2,340, Level: 11 Points: 2,340, Level: 11 Points: 2,340, Level: 11
Activity: 0.4%
Activity: 0.4% Activity: 0.4% Activity: 0.4%
Thanks: Gave 238, Got 546
Posts: 1,863
Re: Yet another boiler question.

Quote:
Originally Posted by the whistler View Post

Occasionally the membrane can be pierced allowing water into the air chamber, which unfortunately means a replacment expansion vessel.
yes what he said, it shouldnt be too difficult to get repaired.

i had the same trouble and rather than fill up to 1.5 BAR as recommended i had to fill it 2.5 / 3 BAR until it was fixed
  Quote
Thanks from:
KoThreads (19-02-2009)
Old 19-02-2009, 1:42 PM   #6
Member
Join Date: Jul 2006
Experience Points:
2,351, Level: 11
Points: 2,351, Level: 11 Points: 2,351, Level: 11 Points: 2,351, Level: 11
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 9, Got 18
Posts: 210
Re: Yet another boiler question.

Had the same problem with a Biasi boiler a few years ago, that was the expansion vessel, cost about £80 for a replacement.
  Quote
Thanks from:
KoThreads (19-02-2009)
Post Reply



Thread information and display options
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off