If you are testing at a socket the problem can be anywhere on the installation. You need to disconnect everything plugged in and disconnect at the board and check individual circuits.
E.g if you have a faulty kettle (neutral-earth) and it is plugged into the installation then you will read that if you are testing at the sockets or on the meter tails. You'd need to unplug it to prevent it showing up or at least switch it off at the socket. Most sockets are double pole. If you are purely testing sockets then unplug everything and test at the board (though in theory you could test anywhere). Bear in mind any fuse spurs on the circuit would also have to be switched off as well.
I've had similar things in the past and it can be down to several things. Possibly a compression fault where a cable is compressed either because it's been jammed into a socket and the neutral cable is worn away at the back of the metal box or on the screw thread securing the socket front, or a cable has been nailed or trapped under something like a florrboard or also once where it was new cable and the very end of the cable had been bashed about and was then used.