Plumbing help needed

Any plumbers / central heating / home hot water / master DIY'er experts out there?

I don't know a great deal about this stuff so I'll just give some details and the symptoms as know them...


The house has a water tank / immersion heater thing (big cylinder thing in a little cupboard) which as far as I can tell handles the hot water for the taps.
there is also a combi boiler which seems to only jump into life when the central heating is on. Its for that reason that believe the immersion heater does the hot water.

Anyways due to the hot weather the central heating has been turned completely off from the timer. Well I guess more acurately, the timer is set to not come on at all so the heating doesn't come on.

But since that, I've not really had an hot water from the taps. Its not freezing cold, as cold as the cold tap water but its not warm and doesn't make for nice showers or shaving. It seems that sometimes the water is hot enough, but its certainly not a case of turn the tap (or shower) on and voila, hot water. It can take ten minutes for the water to warm up sufficiently.

From the immersion tank was a two way lever, one position is central heating, the opposite is hot water. The lever was set to the middle but now I've moved it to Hot Water, but it doesn't seem to have changed anything....

From the plumbing from the cylinder is a electric water pump which I think feeds to the combi boiler.

Thanks in advance folks!!!
  Quote
Old 02-05-2007, 8:43 PM   #2
Senior Member
 
metropolis's Avatar
Join Date: Mar 2006
Location: liverpool
Experience Points:
2,721, Level: 12
Points: 2,721, Level: 12 Points: 2,721, Level: 12 Points: 2,721, Level: 12
Activity: 0.8%
Activity: 0.8% Activity: 0.8% Activity: 0.8%
Thanks: Gave 168, Got 151
Posts: 1,180
Re: Plumbing help needed

are you sure its a combi boiler ? what is the make and model
  Quote
Old 02-05-2007, 8:43 PM   #3
Moderator
 
johnscarlet's Avatar
Join Date: Dec 2002
Location: location location
Experience Points:
18,857, Level: 33
Points: 18,857, Level: 33 Points: 18,857, Level: 33 Points: 18,857, Level: 33
Activity: 20.5%
Activity: 20.5% Activity: 20.5% Activity: 20.5%
Thanks: Gave 224, Got 1,019
Posts: 7,984
Re: Plumbing help needed

Combi boilers don't normally have a tank , the idea is that you heat water while you use it . What make and model is it ?

In the meantime , does the tank have a cable coming from it , somewhere near the top ? if so you could possibly follow it to a switch , which will turn on the electric heating element , But only have it on for as long as necessary , your leccy bill will rocket . Its like boiling a kettle , without the auto turn off

John
  Quote
Old 02-05-2007, 9:17 PM   #4
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Yeah it is a bit odd! There is a fused switch in the airing cupboard which has been on for as long as I've lived here (since 21st december last year). There is one cable from it, which goes to the central heating timer. Another two cables from the timer to the water pump and the combi boiler. There doesn't appear to be any cables from the cylinder.

Must re-iterate the point tha is confusing me most. There was no problem till I stopped using the central heating. Apart from I'm not using that, nothing else has changed or been changed (to my knowledge!).
  Quote
Old 02-05-2007, 9:33 PM   #5
njp njp is offline
Senior Member
Join Date: Oct 2004
Experience Points:
11,560, Level: 25
Points: 11,560, Level: 25 Points: 11,560, Level: 25 Points: 11,560, Level: 25
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 68, Got 178
Posts: 1,497
Re: Plumbing help needed

You've presented a lot of conflicting information. If it's a combi-boiler, you wouldn't need a hot water tank. And why does the water warm up after ten minutes?

If you hadn't said those things, I would have assumed that you have a conventional boiler and the thing with a two way lever is a mid position valve (diverter). This is a motorised valve to control the flow of hot water from the boiler to either the radiators or the hot water cylinder, or both, depending on which system is calling for heat. That in turn depends on thermostats (is there one on the cylinder?) and on the timer controls. Does your controller have a seperate setting for hot water?

In summary: check cylinder thermostat and timer controls first. If they are in order, you may have a faulty diverter valve.
  Quote
Old 02-05-2007, 9:43 PM   #6
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Re: Plumbing help needed

to me it sound like you have an old servo warm system.
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
  Quote
Old 02-05-2007, 9:52 PM   #7
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Quote:
Originally Posted by blitzed View Post
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
yep, thats the one, exactly as you've described!

njp, I know there is a lot of contradictions there and I know I should have one or the other, would normally by the combi boiler. In the future I'm looking at getting rid of the cylinder to knock the cupboard out as it in the kitchen, taking up a lot of room! Could you explain to me how to check the cylinder thermostat please?
  Quote
Old 02-05-2007, 9:55 PM   #8
njp njp is offline
Senior Member
Join Date: Oct 2004
Experience Points:
11,560, Level: 25
Points: 11,560, Level: 25 Points: 11,560, Level: 25 Points: 11,560, Level: 25
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 68, Got 178
Posts: 1,497
Re: Plumbing help needed

Quote:
Originally Posted by shodan View Post
njp, I know there is a lot of contradictions there and I know I should have one or the other, would normally by the combi boiler. In the future I'm looking at getting rid of the cylinder to knock the cupboard out as it in the kitchen, taking up a lot of room! Could you explain to me how to check the cylinder thermostat please?
I think I'll defer to blitzed's greater knowledge. Manual 3 port valves are beyond my experience!
  Quote
Old 02-05-2007, 9:55 PM   #9
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Re: Plumbing help needed

have u tried moving the lever to hot water only and turning the timer on?
this will divert hot water from boiler flow and return circuit to the h/w cylinder only
ed
  Quote
Old 02-05-2007, 10:22 PM   #10
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

I've had a fight with it and managed to move it over to hot water only (it was stuck though, not been moved for ages).

When you say turn the timer on do you mean activate the central heating for a while? Its cold upstairs so I could do that now for 30 mins or so. I'm not sure I understand your last sentence, but then I don't understand how a lot of thins wrk, I'm just happy when they do!
  Quote
Old 02-05-2007, 10:32 PM   #11
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,163, Level: 38
Points: 25,163, Level: 38 Points: 25,163, Level: 38 Points: 25,163, Level: 38
Activity: 33.3%
Activity: 33.3% Activity: 33.3% Activity: 33.3%
Thanks: Gave 2,331, Got 4,981
Posts: 21,271
Re: Plumbing help needed

Quote:
Originally Posted by blitzed View Post
to me it sound like you have an old servo warm system.
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
Spot on that sounds just like what he's got, we had one when we moved into our last house 17 years ago and it didn't work properly then, exactly the same symptoms Shodan has. I stripped out all the Servowarm manual rubbish (that was much touted as being reliable ) and put in a proper electrically controlled valve and thermostat for the house and cylinder. It was still working fine when we left 10 years later.

It sounds to me as if someone who thought they knew what they were doing has fiddled with it to try and improve/mend it without knowing what they were doing. As such you may have inherited a nightmare Shodan. Can you post any photos of wiring etc?

Dave
  Quote
Old 02-05-2007, 10:35 PM   #12
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

what wiring? There really isn't any! the only wires in the cupboard are the one's I've mentioned above. Got me worried now in case there is other wires that I can't see or that are missing!!!!!
  Quote
Old 02-05-2007, 10:38 PM   #13
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,163, Level: 38
Points: 25,163, Level: 38 Points: 25,163, Level: 38 Points: 25,163, Level: 38
Activity: 33.3%
Activity: 33.3% Activity: 33.3% Activity: 33.3%
Thanks: Gave 2,331, Got 4,981
Posts: 21,271
Re: Plumbing help needed

Quote:
Originally Posted by shodan View Post
I've had a fight with it and managed to move it over to hot water only (it was stuck though, not been moved for ages).

When you say turn the timer on do you mean activate the central heating for a while? Its cold upstairs so I could do that now for 30 mins or so. I'm not sure I understand your last sentence, but then I don't understand how a lot of thins wrk, I'm just happy when they do!
If you cranked it over to hot water you shouldn't heat any radiators at all, and if you do it's broke


Yes, turn the boiler on (manual overide the timer?) and just see if the pump vibrates at all and if any pipes in the airing cupboard get warm.

Dave
  Quote
Old 02-05-2007, 10:42 PM   #14
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

will do, stand by!
  Quote
Old 02-05-2007, 10:51 PM   #15
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

ok, the valve selector is set to hot water. the central heating timer is set to 24hours. When I did this, I heard the combi burst into life. The pipes FROM the cylinder are hot to the touch, to and from the valve selector are hot too. Hot water from the tap is warmer than it was, but not hot and still not shower tempreture. Do you think it'll get hotter if I give it some time? Can the system be left in this configuration?
  Quote
Old 02-05-2007, 10:56 PM   #16
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Re: Plumbing help needed

yeh will take at least 20 mins all rads should stay cold.
you need to get that system updated with either a y plan system or s plan system
ed
if your planning to update the system though a combi boiler will replace all this.
your boiler at moment is conventional
  Quote
Old 02-05-2007, 11:03 PM   #17
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Quote:
Originally Posted by blitzed View Post
yeh will take at least 20 mins all rads should stay cold.
you need to get that system updated with either a y plan system or s plan system
ed
if your planning to update the system though a combi boiler will replace all this.
your boiler at moment is conventional
Ah yes, the good old Y plan system... (did I sound like I knew what I was tlaking about? Hee hee hee!). The combi does look old to me so could probably do with being changed...
Do you have any idea's on how much it would cost to get rid of the cylinder and upgrade the combi and some of the tattier looing pipes? Is it one days work? I know someone who could do it for me (I'd be helping, or attempting to) so its just the cost of the supplies...
  Quote
Old 02-05-2007, 11:10 PM   #18
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Thumbs up Re: Plumbing help needed

No disrespect but all work relating to changing boiler etc should only be carried out by Corgi reg'd engineer and it's notifiable to local council(building regs)
but you'd be looking at least 2 days work £800 min
ed
  Quote
Old 02-05-2007, 11:13 PM   #19
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Ah, good shout! I forgot about that! Well, family member is a proper plumber.. I'm sure I could chat him up to do it for me if I got the parts...
So what do you think is the problem then and is it safe to leave the system as it is? Or should I turn off the timer after a little while (as the combi is in full swing) and it'll all be ok from now on? Or until winter...

Sorry for all the questions, but whilst I've got your attention... ;-)
  Quote
Old 02-05-2007, 11:25 PM   #20
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Re: Plumbing help needed

Theres really nothing wrong with the system as such , its just you've have no control over the system every thing has to be done manually,
easiest thing to do would be to get your mate to remove the manual valve and install a mid position valve with room stat and cylinder stat to control your heating and hot water as you need it.

Honeywell do an easy fit system replacing the all the controls.

With regards to leaving the boiler(timer) running id only leave it for 45mins to an hour tops. boiler should cut out on its thermostat when it reaches a set temp but not seeing the system i couldnt comment that well on it.

That manual valve is designed to be moved treat it like a simple summer - winter switch(summer = hot water only, Winter hot water and heating)
  Quote
Thanks from:
shodan (02-05-2007)
Old 02-05-2007, 11:31 PM   #21
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Blitzed, you are a genius and a legend! Thank you so much for your help and advice today! I now have bloody hot water! Do you think it'll be fine from now on? I'll defo take your advice about the easy fit control system replacement. Well, I'll google for it and try to find one!!!!
  Quote
Old 02-05-2007, 11:40 PM   #22
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,163, Level: 38
Points: 25,163, Level: 38 Points: 25,163, Level: 38 Points: 25,163, Level: 38
Activity: 33.3%
Activity: 33.3% Activity: 33.3% Activity: 33.3%
Thanks: Gave 2,331, Got 4,981
Posts: 21,271
Re: Plumbing help needed

We seem to have a good tag team going Blitzed
Only Shodan didn't seem to notice
  Quote
Thanks from:
shodan (02-05-2007)
Old 02-05-2007, 11:42 PM   #23
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Sorry mate, you are absolutely right!! I apologise and massive thanks to you too! Sorry, I've been running all over the place trying to get it sorted! Cheers IronGiant and blitzed!
  Quote
Old 02-05-2007, 11:44 PM   #24
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,163, Level: 38
Points: 25,163, Level: 38 Points: 25,163, Level: 38 Points: 25,163, Level: 38
Activity: 33.3%
Activity: 33.3% Activity: 33.3% Activity: 33.3%
Thanks: Gave 2,331, Got 4,981
Posts: 21,271
Re: Plumbing help needed

No worries Shodan

Your hot water will be fine for the summer, but it's not the cheapest way to do it. get your cousin in ASAP. Or blizted, because he may be a professional, and I'm not

Dave

Last edited by IronGiant; 03-05-2007 at 12:16 AM.
  Quote
Old 03-05-2007, 7:23 AM   #25
njp njp is offline
Senior Member
Join Date: Oct 2004
Experience Points:
11,560, Level: 25
Points: 11,560, Level: 25 Points: 11,560, Level: 25 Points: 11,560, Level: 25
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 68, Got 178
Posts: 1,497
Re: Plumbing help needed

I'm glad the thread has achieved a resolution. But can someone please explain how, given that the boiler was (apparently) switched off, this can be true:

Quote:
Originally Posted by shodan View Post
It seems that sometimes the water is hot enough, but its certainly not a case of turn the tap (or shower) on and voila, hot water. It can take ten minutes for the water to warm up sufficiently.
Or was the warmth just wishful thinking on Shodan's part? Could be a real money-saver!
  Quote
Old 03-05-2007, 11:27 AM   #26
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

The water was definately luke warm. I'm comparing it to how cold the cold water comes out and it was several degree's above that. Well I managed to shower in it without giving myself brain freeze or hyperthermia!!!
  Quote
Old 03-05-2007, 12:11 PM   #27
Moderator
 
IronGiant's Avatar
Join Date: Jun 2003
Location: Oxford UK
Experience Points:
25,163, Level: 38
Points: 25,163, Level: 38 Points: 25,163, Level: 38 Points: 25,163, Level: 38
Activity: 33.3%
Activity: 33.3% Activity: 33.3% Activity: 33.3%
Thanks: Gave 2,331, Got 4,981
Posts: 21,271
Re: Plumbing help needed

Those servowarm systems were completely dependent on the thermostat in the boiler for controlling the temperature of the hot water, so if the manual valve was faulty/stuck and hardly any water was circulating through the cistern the boiler would shut down when it got to temperature, but before the water in the cistern got more than luke warm. So the answer is the boiler must have been on but was rarely switching on once it wasn't circulating hot water to the radiators. Circulating water to the radiators would have kept the temperature down at the boiler allowing it to run long enough to also heat the water up.
  Quote
Old 03-05-2007, 12:11 PM   #28
njp njp is offline
Senior Member
Join Date: Oct 2004
Experience Points:
11,560, Level: 25
Points: 11,560, Level: 25 Points: 11,560, Level: 25 Points: 11,560, Level: 25
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 68, Got 178
Posts: 1,497
Re: Plumbing help needed

Quote:
Originally Posted by shodan View Post
The water was definately luke warm. I'm comparing it to how cold the cold water comes out and it was several degree's above that. Well I managed to shower in it without giving myself brain freeze or hyperthermia!!!
Perhaps you should just unlag your hot water cylinder so that the water reaches room temperature more quickly. Think of the money you'll save!
  Quote
Old 03-05-2007, 5:10 PM   #29
Member
Join Date: Mar 2005
Location: hayes
Experience Points:
2,991, Level: 12
Points: 2,991, Level: 12 Points: 2,991, Level: 12 Points: 2,991, Level: 12
Activity: 0%
Activity: 0% Activity: 0% Activity: 0%
Thanks: Gave 16, Got 11
Posts: 271
Re: Plumbing help needed

been a corgi reg'd heating engineer for 16 years now,
Ive been called out to fault find on these systems more times than i care to remember and its nearly always this valve, or on some very rare occasions the little F&E tank in the corner of the room that needs manually filling

the pack you need is either of the y plan systems:
http://www.discountedheating.co.uk/s...3.html#a310181
  Quote
Old 03-05-2007, 5:38 PM   #30
Prominent Member
 
shodan's Avatar
Join Date: Dec 2001
Location: shoeburyness
Experience Points:
8,215, Level: 21
Points: 8,215, Level: 21 Points: 8,215, Level: 21 Points: 8,215, Level: 21
Activity: 9.1%
Activity: 9.1% Activity: 9.1% Activity: 9.1%
Thanks: Gave 206, Got 578
Posts: 4,842
Re: Plumbing help needed

Once again blitzed, thank you very very much! That link is excellent and incredibly usefull. I shall do some googling and try to learn as much about this stuff as i can...
  Quote
Post Reply



Thread information and display options
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off