Español Français Deutsch Italiano Nederlands Svenska Dansk Japanese Chinese (Simplified) Russian
 
AVForums.com twitter AVForums is a member of CEDIA. THX certified reviewer.  Click for more information. AVForums reviewers are ISF Certified.  Click for more information.
 
The UK's biggest and best home entertainment electronics forums  
4 million visitors each month


Forums Register Blogs Information Social Groups Search Today's Posts Mark Forums Read
Go Back   AVForums.com > Lifestyle Topics > General Chat

Latest AVForums Movie Reviews
Terminator Salvation Blu-ray ReviewGray Lady Down - Original Motion Picture Soundtrack CD ReviewUp Blu-ray ReviewLéon Blu-ray ReviewNear Dark Blu-ray Review
Logan's Run Blu-ray ReviewTaking of Pelham 1 2 3, The Blu-ray ReviewStar Trek Blu-ray ReviewUFC 100: Lesnar vs. Mir (2009) Blu-ray ReviewThe New York Ripper Blu-ray Review


Reply
 
Thread Tools Display Modes
Old 02-05-2007, 8:37 PM   #1 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Plumbing help needed

Any plumbers / central heating / home hot water / master DIY'er experts out there?

I don't know a great deal about this stuff so I'll just give some details and the symptoms as know them...


The house has a water tank / immersion heater thing (big cylinder thing in a little cupboard) which as far as I can tell handles the hot water for the taps.
there is also a combi boiler which seems to only jump into life when the central heating is on. Its for that reason that believe the immersion heater does the hot water.

Anyways due to the hot weather the central heating has been turned completely off from the timer. Well I guess more acurately, the timer is set to not come on at all so the heating doesn't come on.

But since that, I've not really had an hot water from the taps. Its not freezing cold, as cold as the cold tap water but its not warm and doesn't make for nice showers or shaving. It seems that sometimes the water is hot enough, but its certainly not a case of turn the tap (or shower) on and voila, hot water. It can take ten minutes for the water to warm up sufficiently.

From the immersion tank was a two way lever, one position is central heating, the opposite is hot water. The lever was set to the middle but now I've moved it to Hot Water, but it doesn't seem to have changed anything....

From the plumbing from the cylinder is a electric water pump which I think feeds to the combi boiler.

Thanks in advance folks!!!
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 8:43 PM   #2 (permalink)
Member
 
metropolis's Avatar
 
Join Date: Mar 2006
Posts: 335
Thanks: Gave 50, Got 54
Re: Plumbing help needed

are you sure its a combi boiler ? what is the make and model
metropolis is offline   Reply With Quote
Old 02-05-2007, 8:43 PM   #3 (permalink)
Moderator
 
Join Date: Dec 2002
Location: Our house , in the middle of our street
Posts: 3,888
Thanks: Gave 111, Got 444
Re: Plumbing help needed

Combi boilers don't normally have a tank , the idea is that you heat water while you use it . What make and model is it ?

In the meantime , does the tank have a cable coming from it , somewhere near the top ? if so you could possibly follow it to a switch , which will turn on the electric heating element , But only have it on for as long as necessary , your leccy bill will rocket . Its like boiling a kettle , without the auto turn off

John
__________________
My opinions expressed here do not represent those of the AV Forums or it's associated websites

Need a TV Guide ? Look here.
johnscarlet is offline   Reply With Quote
Old 02-05-2007, 9:17 PM   #4 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

Yeah it is a bit odd! There is a fused switch in the airing cupboard which has been on for as long as I've lived here (since 21st december last year). There is one cable from it, which goes to the central heating timer. Another two cables from the timer to the water pump and the combi boiler. There doesn't appear to be any cables from the cylinder.

Must re-iterate the point tha is confusing me most. There was no problem till I stopped using the central heating. Apart from I'm not using that, nothing else has changed or been changed (to my knowledge!).
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 9:33 PM   #5 (permalink)
njp
Senior Member
 
Join Date: Oct 2004
Posts: 2,139
Thanks: Gave 68, Got 178
Re: Plumbing help needed

You've presented a lot of conflicting information. If it's a combi-boiler, you wouldn't need a hot water tank. And why does the water warm up after ten minutes?

If you hadn't said those things, I would have assumed that you have a conventional boiler and the thing with a two way lever is a mid position valve (diverter). This is a motorised valve to control the flow of hot water from the boiler to either the radiators or the hot water cylinder, or both, depending on which system is calling for heat. That in turn depends on thermostats (is there one on the cylinder?) and on the timer controls. Does your controller have a seperate setting for hot water?

In summary: check cylinder thermostat and timer controls first. If they are in order, you may have a faulty diverter valve.
njp is offline   Reply With Quote
Old 02-05-2007, 9:43 PM   #6 (permalink)
Member
 
Join Date: Mar 2005
Location: london
Posts: 253
Thanks: Gave 14, Got 11
Re: Plumbing help needed

to me it sound like you have an old servo warm system.
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
blitzed is offline   Reply With Quote
Old 02-05-2007, 9:52 PM   #7 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

Quote:
Originally Posted by blitzed View Post
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
yep, thats the one, exactly as you've described!

njp, I know there is a lot of contradictions there and I know I should have one or the other, would normally by the combi boiler. In the future I'm looking at getting rid of the cylinder to knock the cupboard out as it in the kitchen, taking up a lot of room! Could you explain to me how to check the cylinder thermostat please?
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 9:55 PM   #8 (permalink)
njp
Senior Member
 
Join Date: Oct 2004
Posts: 2,139
Thanks: Gave 68, Got 178
Re: Plumbing help needed

Quote:
Originally Posted by shodan View Post
njp, I know there is a lot of contradictions there and I know I should have one or the other, would normally by the combi boiler. In the future I'm looking at getting rid of the cylinder to knock the cupboard out as it in the kitchen, taking up a lot of room! Could you explain to me how to check the cylinder thermostat please?
I think I'll defer to blitzed's greater knowledge. Manual 3 port valves are beyond my experience!
njp is offline   Reply With Quote
Old 02-05-2007, 9:55 PM   #9 (permalink)
Member
 
Join Date: Mar 2005
Location: london
Posts: 253
Thanks: Gave 14, Got 11
Re: Plumbing help needed

have u tried moving the lever to hot water only and turning the timer on?
this will divert hot water from boiler flow and return circuit to the h/w cylinder only
ed
blitzed is offline   Reply With Quote
Old 02-05-2007, 10:22 PM   #10 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

I've had a fight with it and managed to move it over to hot water only (it was stuck though, not been moved for ages).

When you say turn the timer on do you mean activate the central heating for a while? Its cold upstairs so I could do that now for 30 mins or so. I'm not sure I understand your last sentence, but then I don't understand how a lot of thins wrk, I'm just happy when they do!
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 10:32 PM   #11 (permalink)
Moderator
 
IronGiant's Avatar
 
Join Date: Jun 2003
Location: Oxford UK
Posts: 3,570
Thanks: Gave 582, Got 1,554
Re: Plumbing help needed

Quote:
Originally Posted by blitzed View Post
to me it sound like you have an old servo warm system.
was the lever thing a manual control (looks like a round cylindrical thing with lever sticking out sometimes has red and yellow on it).?
Spot on that sounds just like what he's got, we had one when we moved into our last house 17 years ago and it didn't work properly then, exactly the same symptoms Shodan has. I stripped out all the Servowarm manual rubbish (that was much touted as being reliable ) and put in a proper electrically controlled valve and thermostat for the house and cylinder. It was still working fine when we left 10 years later.

It sounds to me as if someone who thought they knew what they were doing has fiddled with it to try and improve/mend it without knowing what they were doing. As such you may have inherited a nightmare Shodan. Can you post any photos of wiring etc?

Dave
__________________
We all stand on the shoulders of giants...

My personal opinion is not necessarily AVF policy.
IronGiant is offline   Reply With Quote
Old 02-05-2007, 10:35 PM   #12 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

what wiring? There really isn't any! the only wires in the cupboard are the one's I've mentioned above. Got me worried now in case there is other wires that I can't see or that are missing!!!!!
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 10:38 PM   #13 (permalink)
Moderator
 
IronGiant's Avatar
 
Join Date: Jun 2003
Location: Oxford UK
Posts: 3,570
Thanks: Gave 582, Got 1,554
Re: Plumbing help needed

Quote:
Originally Posted by shodan View Post
I've had a fight with it and managed to move it over to hot water only (it was stuck though, not been moved for ages).

When you say turn the timer on do you mean activate the central heating for a while? Its cold upstairs so I could do that now for 30 mins or so. I'm not sure I understand your last sentence, but then I don't understand how a lot of thins wrk, I'm just happy when they do!
If you cranked it over to hot water you shouldn't heat any radiators at all, and if you do it's broke


Yes, turn the boiler on (manual overide the timer?) and just see if the pump vibrates at all and if any pipes in the airing cupboard get warm.

Dave
__________________
We all stand on the shoulders of giants...

My personal opinion is not necessarily AVF policy.
IronGiant is offline   Reply With Quote
Old 02-05-2007, 10:42 PM   #14 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

will do, stand by!
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote
Old 02-05-2007, 10:51 PM   #15 (permalink)
Senior Member
 
shodan's Avatar
 
Join Date: Dec 2001
Location: shoeburyness
Posts: 1,363
Thanks: Gave 59, Got 231
Re: Plumbing help needed

ok, the valve selector is set to hot water. the central heating timer is set to 24hours. When I did this, I heard the combi burst into life. The pipes FROM the cylinder are hot to the touch, to and from the valve selector are hot too. Hot water from the tap is warmer than it was, but not hot and still not shower tempreture. Do you think it'll get hotter if I give it some time? Can the system be left in this configuration?
__________________
Can't think of anything funny to say...
shodan is offline   Reply With Quote



Bookmarks

Tags
needed, plumbing
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


All times are GMT. The time now is 7:46 AM.

AV Forums
Optimised for Firefox.
RSS Feed
AVForums.com is owned and operated by M2N Limited.
Copyright © 2000-2009 M2N E. & O. E.
Global Gold
Web Hosting